ParticipantHi there, I’m trying to use a Danfoss living connect Z SDK 4.55 soft version 1.01 Product ID 4
I can change the wake interval without any problem. That seems to be working. I get the heating 1 value from the radiator thermostat. But when I want to set the radiator value, i allways get the value 4 on the thermostat, not the requested value.
Anyone has experience with this radiator thermostat? Other suggestions?November 10, 2015 at 6:28 pm #1728dirk_dedeur
ParticipantI have been checking the zwave log, after setting the heating 1 value from 20 to 18 i see in the log that the software changes the value from 20 to 4
Refreshed Value: old value=20.00, new value=4.00, type=string
2015-11-10 17:09:46.790 Detail, Node007, Removing current message
2015-11-10 17:09:46.790 Detail,
2015-11-10 17:09:46.790 Info, Node007, Sending (WakeUp) message (Callback ID=0x0c, Expected Reply=0x04) – ThermostatSetpointCmd_Get (Node=7): 0x01, 0x0a, 0x00, 0x13, 0x07, 0x03, 0x43, 0x02, 0x01, 0x25, 0x0c, 0x8b
2015-11-10 17:09:46.796 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
2015-11-10 17:09:46.796 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
2015-11-10 17:09:46.808 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x0c, 0x00, 0xe5
2015-11-10 17:09:46.808 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x0c received (expected 0x0c)
2015-11-10 17:09:46.808 Info, Node007, Request RTT 17 Average Request RTT 17
2015-11-10 17:09:46.808 Detail, Expected callbackId was received
2015-11-10 17:09:46.823 Detail, Node007, Received: 0x01, 0x0c, 0x00, 0x04, 0x00, 0x07, 0x06, 0x43, 0x03, 0x01, 0x42, 0x01, 0x90, 0x64
2015-11-10 17:09:46.823 Detail,
2015-11-10 17:09:46.823 Info, Node007, Response RTT 32 Average Response RTT 92
2015-11-10 17:09:46.823 Detail, Node007, Refreshed Value: old value=20.00, new value=4.00, type=string
2015-11-10 17:09:46.823 Detail, Node007, Changes to this value are not verified
2015-11-10 17:09:46.823 Info, Node007, Received thermostat setpoint report: Setpoint Heating 1 = 4.00C
2015-11-10 17:09:46.823 Detail, Node007, Expected reply and command class was received
2015-11-10 17:09:46.823 Detail, Node007, Message transaction complete
2015-11-10 17:09:46.823 Detail,
2015-11-10 17:09:46.824 Detail, Node007, Removing current message
2015-11-10 17:09:46.824 Detail, Node007, Notification: ValueChanged
2015-11-10 17:09:47.189 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 67-user-decimal-1-1
2015-11-10 17:09:47.264 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:47.709 Detail,
2015-11-10 17:09:47.709 Info, Node007, Sending (WakeUp) message (Callback ID=0x1d, Expected Reply=0x04) – BatteryCmd_Get (Node=7): 0x01, 0x09, 0x00, 0x13, 0x07, 0x02, 0x80, 0x02, 0x25, 0x1d, 0x5a
2015-11-10 17:09:47.715 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
2015-11-10 17:09:47.715 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
2015-11-10 17:09:47.726 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x1d, 0x00, 0xf4
2015-11-10 17:09:47.726 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x1d received (expected 0x1d)
2015-11-10 17:09:47.727 Info, Node007, Request RTT 17 Average Request RTT 17
2015-11-10 17:09:47.727 Detail, Expected callbackId was received
2015-11-10 17:09:47.734 Detail, Node007, Received: 0x01, 0x09, 0x00, 0x04, 0x00, 0x07, 0x03, 0x80, 0x03, 0x3c, 0x49
2015-11-10 17:09:47.734 Detail,
2015-11-10 17:09:47.734 Info, Node007, Response RTT 25 Average Response RTT 58
2015-11-10 17:09:47.734 Info, Node007, Received Battery report from node 7: level=60
2015-11-10 17:09:47.734 Detail, Node007, Refreshed Value: old value=60, new value=60, type=uint8
2015-11-10 17:09:47.734 Detail, Node007, Changes to this value are not verified
2015-11-10 17:09:47.734 Detail, Node007, Expected reply and command class was received
2015-11-10 17:09:47.734 Detail, Node007, Message transaction complete
2015-11-10 17:09:47.734 Detail,
2015-11-10 17:09:47.735 Detail, Node007, Removing current message
2015-11-10 17:09:47.735 Detail, Node007, Notification: ValueChanged
2015-11-10 17:09:48.031 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 128-user-byte-1-0
2015-11-10 17:09:48.102 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:48.601 Detail,
2015-11-10 17:09:48.601 Info, Node007, Sending (WakeUp) message (Callback ID=0x1e, Expected Reply=0x04) – ClockCmd_Get (Node=7): 0x01, 0x09, 0x00, 0x13, 0x07, 0x02, 0x81, 0x05, 0x25, 0x1e, 0x5f
2015-11-10 17:09:48.607 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
2015-11-10 17:09:48.607 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
2015-11-10 17:09:48.619 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x1e, 0x00, 0xf7
2015-11-10 17:09:48.619 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x1e received (expected 0x1e)
2015-11-10 17:09:48.619 Info, Node007, Request RTT 17 Average Request RTT 17
2015-11-10 17:09:48.619 Detail, Expected callbackId was received
2015-11-10 17:09:48.626 Detail, Node007, Received: 0x01, 0x0a, 0x00, 0x04, 0x00, 0x07, 0x04, 0x81, 0x06, 0xf2, 0x21, 0xa6
2015-11-10 17:09:48.626 Detail,
2015-11-10 17:09:48.626 Info, Node007, Response RTT 24 Average Response RTT 41
2015-11-10 17:09:48.626 Info, Node007, Received Clock report: Sunday 18:33
2015-11-10 17:09:48.626 Detail, Node007, Refreshed Value: old value=6, new value=6, type=int32
2015-11-10 17:09:48.626 Detail, Node007, Changes to this value are not verified
2015-11-10 17:09:48.626 Detail, Node007, Refreshed Value: old value=18, new value=18, type=uint8
2015-11-10 17:09:48.627 Detail, Node007, Changes to this value are not verified
2015-11-10 17:09:48.627 Detail, Node007, Refreshed Value: old value=19, new value=33, type=uint8
2015-11-10 17:09:48.627 Detail, Node007, Changes to this value are not verified
2015-11-10 17:09:48.627 Detail, Node007, Expected reply and command class was received
2015-11-10 17:09:48.627 Detail, Node007, Message transaction complete
2015-11-10 17:09:48.627 Detail,
2015-11-10 17:09:48.629 Detail, Node007, Removing current message
2015-11-10 17:09:48.630 Detail, Node007, Notification: ValueChanged
2015-11-10 17:09:48.970 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-list-1-0
2015-11-10 17:09:49.012 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:49.417 Detail, Node007, Notification: ValueChanged
2015-11-10 17:09:49.769 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-byte-1-1
2015-11-10 17:09:49.796 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:50.187 Detail, Node007, Notification: ValueChanged
2015-11-10 17:09:50.574 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-byte-1-2
2015-11-10 17:09:50.617 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:51.134 Detail, Node007, Query Stage Complete (Dynamic)
2015-11-10 17:09:51.134 Detail, Node007, AdvanceQueries queryPending=0 queryRetries=0 queryStage=Configuration live=1
2015-11-10 17:09:51.134 Detail, Node007, QueryStage_Configuration
2015-11-10 17:09:51.134 Detail, Node007, QueryStage_Complete
2015-11-10 17:09:51.134 Warning, CheckCompletedNodeQueries m_allNodesQueried=0 m_awakeNodesQueried=1
2015-11-10 17:09:51.134 Warning, CheckCompletedNodeQueries all=0, deadFound=0 sleepingOnly=1
2015-11-10 17:09:51.135 Detail, Node007, Notification: NodeQueriesComplete
2015-11-10 17:09:51.198 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
2015-11-10 17:09:51.912 Detail, Node009, Received: 0x01, 0x09, 0x00, 0x04, 0x00, 0x09, 0x03, 0x80, 0x03, 0x47, 0x3c
2015-11-10 17:09:51.913 Detail,
2015-11-10 17:09:51.913 Info, Node009, Received Battery report from node 9: level=71
2015-11-10 17:09:51.913 Detail, Node009, Refreshed Value: old value=71, new value=71, type=uint8November 14, 2015 at 7:58 am #1757Mika
KeymasterI have a danfoss somewhere in my devices, I’ll test it again…
November 22, 2015 at 11:47 am #1898dirk_dedeur
ParticipantI executed the Zwave update but without any change. Anyone who knows how to use the Danfoss Living connect Z? I’m changing the heating1 values. Maybe it’s not the correct way…
December 8, 2015 at 10:09 pm #2087dirk_dedeur
ParticipantCould you test it again Mika, i still don’t get any result…
December 27, 2015 at 1:42 am #2224Propane
ParticipantHi,
You can set the temperature setpoint for Danfoss Living Z like this:
0x01, 0x0d, 0x00, 0x13, nodeID, 0x06, 0x43, 0x01, 0x01, 0x42, Temp1, Temp2, 0x25, 0xd1, Checksum
where Temp1 and Temp2 are = Temperature_Setpoint * 100 (in °C). Example 0x07, 0xD0 is 20°C.
I have a question; Could you please give the hex sequence how to change the wake-up interval?
-