Danfoss Living connect Z

Domotica gratuit Forums Report a bug Danfoss Living connect Z

Mots-clés : 

Ce sujet a 5 réponses, 3 participants et a été mis à jour par  Propane, il y a 1 an et 9 mois.

6 sujets de 1 à 6 (sur un total de 6)
  • Auteur
    Messages
  • #1723

    dirk_dedeur
    Participant

    Hi there, I’m trying to use a Danfoss living connect Z SDK 4.55 soft version 1.01 Product ID 4

    I can change the wake interval without any problem. That seems to be working. I get the heating 1 value from the radiator thermostat. But when I want to set the radiator value, i allways get the value 4 on the thermostat, not the requested value.
    Anyone has experience with this radiator thermostat? Other suggestions?

    #1728

    dirk_dedeur
    Participant

    I have been checking the zwave log, after setting the heating 1 value from 20 to 18 i see in the log that the software changes the value from 20 to 4

    Refreshed Value: old value=20.00, new value=4.00, type=string

    2015-11-10 17:09:46.790 Detail, Node007, Removing current message
    2015-11-10 17:09:46.790 Detail,
    2015-11-10 17:09:46.790 Info, Node007, Sending (WakeUp) message (Callback ID=0x0c, Expected Reply=0x04) – ThermostatSetpointCmd_Get (Node=7): 0x01, 0x0a, 0x00, 0x13, 0x07, 0x03, 0x43, 0x02, 0x01, 0x25, 0x0c, 0x8b
    2015-11-10 17:09:46.796 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
    2015-11-10 17:09:46.796 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
    2015-11-10 17:09:46.808 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x0c, 0x00, 0xe5
    2015-11-10 17:09:46.808 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x0c received (expected 0x0c)
    2015-11-10 17:09:46.808 Info, Node007, Request RTT 17 Average Request RTT 17
    2015-11-10 17:09:46.808 Detail, Expected callbackId was received
    2015-11-10 17:09:46.823 Detail, Node007, Received: 0x01, 0x0c, 0x00, 0x04, 0x00, 0x07, 0x06, 0x43, 0x03, 0x01, 0x42, 0x01, 0x90, 0x64
    2015-11-10 17:09:46.823 Detail,
    2015-11-10 17:09:46.823 Info, Node007, Response RTT 32 Average Response RTT 92
    2015-11-10 17:09:46.823 Detail, Node007, Refreshed Value: old value=20.00, new value=4.00, type=string
    2015-11-10 17:09:46.823 Detail, Node007, Changes to this value are not verified
    2015-11-10 17:09:46.823 Info, Node007, Received thermostat setpoint report: Setpoint Heating 1 = 4.00C
    2015-11-10 17:09:46.823 Detail, Node007, Expected reply and command class was received
    2015-11-10 17:09:46.823 Detail, Node007, Message transaction complete
    2015-11-10 17:09:46.823 Detail,
    2015-11-10 17:09:46.824 Detail, Node007, Removing current message
    2015-11-10 17:09:46.824 Detail, Node007, Notification: ValueChanged
    2015-11-10 17:09:47.189 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 67-user-decimal-1-1
    2015-11-10 17:09:47.264 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:47.709 Detail,
    2015-11-10 17:09:47.709 Info, Node007, Sending (WakeUp) message (Callback ID=0x1d, Expected Reply=0x04) – BatteryCmd_Get (Node=7): 0x01, 0x09, 0x00, 0x13, 0x07, 0x02, 0x80, 0x02, 0x25, 0x1d, 0x5a
    2015-11-10 17:09:47.715 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
    2015-11-10 17:09:47.715 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
    2015-11-10 17:09:47.726 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x1d, 0x00, 0xf4
    2015-11-10 17:09:47.726 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x1d received (expected 0x1d)
    2015-11-10 17:09:47.727 Info, Node007, Request RTT 17 Average Request RTT 17
    2015-11-10 17:09:47.727 Detail, Expected callbackId was received
    2015-11-10 17:09:47.734 Detail, Node007, Received: 0x01, 0x09, 0x00, 0x04, 0x00, 0x07, 0x03, 0x80, 0x03, 0x3c, 0x49
    2015-11-10 17:09:47.734 Detail,
    2015-11-10 17:09:47.734 Info, Node007, Response RTT 25 Average Response RTT 58
    2015-11-10 17:09:47.734 Info, Node007, Received Battery report from node 7: level=60
    2015-11-10 17:09:47.734 Detail, Node007, Refreshed Value: old value=60, new value=60, type=uint8
    2015-11-10 17:09:47.734 Detail, Node007, Changes to this value are not verified
    2015-11-10 17:09:47.734 Detail, Node007, Expected reply and command class was received
    2015-11-10 17:09:47.734 Detail, Node007, Message transaction complete
    2015-11-10 17:09:47.734 Detail,
    2015-11-10 17:09:47.735 Detail, Node007, Removing current message
    2015-11-10 17:09:47.735 Detail, Node007, Notification: ValueChanged
    2015-11-10 17:09:48.031 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 128-user-byte-1-0
    2015-11-10 17:09:48.102 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:48.601 Detail,
    2015-11-10 17:09:48.601 Info, Node007, Sending (WakeUp) message (Callback ID=0x1e, Expected Reply=0x04) – ClockCmd_Get (Node=7): 0x01, 0x09, 0x00, 0x13, 0x07, 0x02, 0x81, 0x05, 0x25, 0x1e, 0x5f
    2015-11-10 17:09:48.607 Detail, Node007, Received: 0x01, 0x04, 0x01, 0x13, 0x01, 0xe8
    2015-11-10 17:09:48.607 Detail, Node007, ZW_SEND_DATA delivered to Z-Wave stack
    2015-11-10 17:09:48.619 Detail, Node007, Received: 0x01, 0x05, 0x00, 0x13, 0x1e, 0x00, 0xf7
    2015-11-10 17:09:48.619 Detail, Node007, ZW_SEND_DATA Request with callback ID 0x1e received (expected 0x1e)
    2015-11-10 17:09:48.619 Info, Node007, Request RTT 17 Average Request RTT 17
    2015-11-10 17:09:48.619 Detail, Expected callbackId was received
    2015-11-10 17:09:48.626 Detail, Node007, Received: 0x01, 0x0a, 0x00, 0x04, 0x00, 0x07, 0x04, 0x81, 0x06, 0xf2, 0x21, 0xa6
    2015-11-10 17:09:48.626 Detail,
    2015-11-10 17:09:48.626 Info, Node007, Response RTT 24 Average Response RTT 41
    2015-11-10 17:09:48.626 Info, Node007, Received Clock report: Sunday 18:33
    2015-11-10 17:09:48.626 Detail, Node007, Refreshed Value: old value=6, new value=6, type=int32
    2015-11-10 17:09:48.626 Detail, Node007, Changes to this value are not verified
    2015-11-10 17:09:48.626 Detail, Node007, Refreshed Value: old value=18, new value=18, type=uint8
    2015-11-10 17:09:48.627 Detail, Node007, Changes to this value are not verified
    2015-11-10 17:09:48.627 Detail, Node007, Refreshed Value: old value=19, new value=33, type=uint8
    2015-11-10 17:09:48.627 Detail, Node007, Changes to this value are not verified
    2015-11-10 17:09:48.627 Detail, Node007, Expected reply and command class was received
    2015-11-10 17:09:48.627 Detail, Node007, Message transaction complete
    2015-11-10 17:09:48.627 Detail,
    2015-11-10 17:09:48.629 Detail, Node007, Removing current message
    2015-11-10 17:09:48.630 Detail, Node007, Notification: ValueChanged
    2015-11-10 17:09:48.970 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-list-1-0
    2015-11-10 17:09:49.012 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:49.417 Detail, Node007, Notification: ValueChanged
    2015-11-10 17:09:49.769 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-byte-1-1
    2015-11-10 17:09:49.796 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:50.187 Detail, Node007, Notification: ValueChanged
    2015-11-10 17:09:50.574 Info, Notification: Value Changed – Add DB Record for device id zwave-7 and value id 129-user-byte-1-2
    2015-11-10 17:09:50.617 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:51.134 Detail, Node007, Query Stage Complete (Dynamic)
    2015-11-10 17:09:51.134 Detail, Node007, AdvanceQueries queryPending=0 queryRetries=0 queryStage=Configuration live=1
    2015-11-10 17:09:51.134 Detail, Node007, QueryStage_Configuration
    2015-11-10 17:09:51.134 Detail, Node007, QueryStage_Complete
    2015-11-10 17:09:51.134 Warning, CheckCompletedNodeQueries m_allNodesQueried=0 m_awakeNodesQueried=1
    2015-11-10 17:09:51.134 Warning, CheckCompletedNodeQueries all=0, deadFound=0 sleepingOnly=1
    2015-11-10 17:09:51.135 Detail, Node007, Notification: NodeQueriesComplete
    2015-11-10 17:09:51.198 Info, mgr, Manager::WriteConfig completed for driver with home ID of 0x0184df35
    2015-11-10 17:09:51.912 Detail, Node009, Received: 0x01, 0x09, 0x00, 0x04, 0x00, 0x09, 0x03, 0x80, 0x03, 0x47, 0x3c
    2015-11-10 17:09:51.913 Detail,
    2015-11-10 17:09:51.913 Info, Node009, Received Battery report from node 9: level=71
    2015-11-10 17:09:51.913 Detail, Node009, Refreshed Value: old value=71, new value=71, type=uint8

    #1757
    Mika
    Mika
    Admin bbPress

    I have a danfoss somewhere in my devices, I’ll test it again…

    #1898

    dirk_dedeur
    Participant

    I executed the Zwave update but without any change. Anyone who knows how to use the Danfoss Living connect Z? I’m changing the heating1 values. Maybe it’s not the correct way…

    #2087

    dirk_dedeur
    Participant

    Could you test it again Mika, i still don’t get any result…

    #2224

    Propane
    Participant

    Hi,

    You can set the temperature setpoint for Danfoss Living Z like this:

    0x01, 0x0d, 0x00, 0x13, nodeID, 0x06, 0x43, 0x01, 0x01, 0x42, Temp1, Temp2, 0x25, 0xd1, Checksum

    where Temp1 and Temp2 are = Temperature_Setpoint * 100 (in °C). Example 0x07, 0xD0 is 20°C.

    I have a question; Could you please give the hex sequence how to change the wake-up interval?